Describe an emergency electrical power generating plant for use if the main electrical power fails, covering location, starting arrangements, fuel oil and supply, cooling system, and periodic attentio
Short answer
flowchart TD
A[Main power failure] --> B[Automatic start signal]
B --> C[Emergency generator starts]
C --> D[Connects to emergency switchboard]
D --> E[Supplies emergency services]
E --> F[Full-load test weekly]
F --> G[Simulated blackout test monthly]
- Location: above the uppermost continuous deck, readily accessible from the open deck, not forward of the collision bulkhead
- Starting: independent means; automatic on loss of main power; battery for small sets, compressed air for larger sets; connect to emergency switchboard automatically; within 45 s
- Fuel: independent supply; flashpoint not less than 43°C
- Cooling: independent freshwater system with heat exchanger, or keel cooling; designed to function at list up to 22.5° and trim up to 10°
- Periodic attention: full-load and starting-time tests under simulated blackout; routine on-load tests
- Governing instrument: SOLAS Chapter II-1 Regulation 42; IMO Res. A.1023(26) ch-5 §5.4.8