In a ship’s power system, why is the low voltage neutral not grounded while the high voltage neutral must be grounded, and what are the different earthing arrangements for HV systems?

Short answer

flowchart TD
    A[IT earth system] -->|Single earth fault| B[No disconnection]
    A -->|Second earth fault| C[Protection operates]
    D[Earthed neutral HV] -->|Resistor| E[Limited fault current]
    D -->|Solid| F[Direct to hull]
    D -->|Divided| G[Neutral-to-hull per section]
  • Low voltage earthing: Ships employ an IT earth system; a single earth fault does not disconnect supply, a second fault causes protection to operate (Rec 137 §2.1)
  • High voltage earthing: Neutral of AC networks of 3000 V line-to-line and over may be earthed; HV systems are normally earthed via a resistor (SOLAS II-1 Reg 45 §4.1, TEAP Part B Appendix III/9.2)
  • Fault current limit: Earth fault current not greater than full-load current of the largest generator, not less than three times the minimum earth-fault protection operating current; at least one neutral-to-ground connection must be available when energized (UR E11 §2.1.2)
  • Divided systems: In systems with neutral earthed, a neutral-to-hull connection is to be provided for each section (UR E11 §2.1.5)
  • Tankers: Earthed distribution systems shall not be used; HV neutral earthing is permitted only if fault current does not flow through dangerous spaces (SOLAS II-1 Reg 45 §4.1)
  • Hull return: The ship’s hull is not to be used as a current-carrying conductor; systems are to be wired as insulated return systems (UK chap6rev3/4 §6.2.5)