With reference to an emergency fire pump, state the regulations for its location, capacity and power, how its power supply is ensured, and why a relief valve is necessary on the deck main?

Updated · AI-generated answer

Short answer

  • Purpose: Emergency fire pump provides fire-fighting capability when main fire pumps are inoperable due to fire in machinery spaces
  • Location: SOLAS II-2/10.2.2.3.2 — space not contiguous to category A machinery spaces; UI SC245 — pump, seawater inlet, suction/delivery pipes outside machinery space
  • Capacity: SOLAS II-2/10.2.2.4.2 — each pump ≥80% of total required capacity divided by minimum number, but ≥25 m³/h; FSS Code ch-12 — emergency pump ≥40% of total fire pump capacity, minimum 25 m³/h (≥2000 GT) or 15 m³/h (<2000 GT)
  • Power: SOLAS II-2/10.2.2.3.2 — independent source of power; FSS Code ch-12 — fixed independently driven power-operated pump
  • Power supply: UR E15 — electrical services operable under fire; pump, sea suctions, priming means, power sources, switchboards, cables not in main fire pump compartment
  • Relief valve: A.1023(26) ch-9 §9.7.9 — relief valves required on all pumps connected to fire main if capable of exceeding fire main design pressure
  • ETO role: Ensure electrical power supply meets fire resistance and independence requirements; maintain and test systems per SMS
flowchart TD
    A[Emergency Fire Pump] --> B["Location: Outside machinery space
SOLAS II-2/10.2.2.3.2
UI SC245"] A --> C["Capacity: ≥40% total fire pump capacity
FSS ch-12"] A --> D["Power: Independent source
SOLAS II-2/10.2.2.3.2"] B --> E["Piping: Suction/delivery outside machinery space"] D --> F["Power Supply: Cables/switchboards outside
UR E15"] A --> G["Deck Main Relief Valve: A.1023(26) ch-9 §9.7.9"]

Rules mentioned: SOLAS

How this answer is built

The rules and references the full answer draws on, from international rules down to practice on board.

The full answer draws on6 sources in 3 groups
  1. International rules (IMO)Conventions, codes, resolutions and circulars
    • SOLAS Chapter II-2Reg 10 para 2.2.3.2 · Reg 10 para 2.2.4.2
    • FSSChapter 12 · Chapter 12 para 2
    • A.1023(26)Chapter 9 §9.7.9
  2. Class society (IACS)Unified requirements, interpretations and recommendations
    • IACS UI SC245Regulation 10.2.1.4.1
  3. Engineering practiceHow it is done on board
    • E15 §1 — Electrical services required to be operable under fire conditions are as follows
    • Emergency fire pump

Full answer

The full answer explains each point step by step, with the regulations and figures behind it and the discussion from other candidates. It is in the ETO section of the Marine One forum, open to members enrolled for the ETO exam.