What is boiler accumulation pressure test?

Short answer

flowchart TD
    A[Start full firing] --> B[Shut off feed water]
    B --> C[Close all stop valves]
    C --> D[Isolate from other boilers]
    D --> E[Run test: ≤15 min shell / ≤7 min water-tube]
    E --> F{Accumulation ≤10% working pressure?}
    F -->|Yes| G[Test passed]
    F -->|No| H[Test failed]
  • Definition: test that checks how fast pressure rises in a boiler when steam generation continues with feed water shut off
  • Purpose: verify safety valves can relieve steam fast enough to prevent overpressure
  • Conditions: full firing, feed water shut off, all stop valves closed, no communication between boilers
  • Duration: ≤15 min for shell boilers, ≤7 min for water-tube boilers
  • Acceptance: pressure accumulation must not exceed 10% of the working pressure
  • Special cases: waste-heat boilers tested at max engine load; composite boilers under full firing
  • IMO basis: SOLAS 74/88 Regulation II-1/26 requires pressure tests for boilers and systems under internal pressure

Full answer

The full answer explains each point step by step, with the regulations and figures behind it and the discussion from other candidates. It is in the MEO Class II section of the Marine One forum, open to members enrolled for the MEO Class II exam.