As chief engineer, what actions do you take if low insulation is detected in submersible cargo pumps?
Short answer
flowchart TD
A[Detect low insulation] --> B{< 1.0 MΩ?}
B -->|Yes| C[Isolate pump motor]
B -->|No| D[Monitor]
C --> E[Megger test each cable]
E --> F{Water ingress?}
F -->|Yes| G[Repair/replace cable]
F -->|No| H[Check motor windings]
G --> I[Verify >1.0 MΩ]
H --> I
I --> J[Update electrical log]
J --> K[Notify cargo control station]
- Threshold: insulation resistance < 1.0 MΩ for systems > 50 V, < 0.3 MΩ for ≤ 50 V
- IGC Code: submersible pump motors in containment must auto-shutdown on low liquid level and be isolatable for gas-freeing
- Immediate action: isolate pump motor from electrical supply, verify with megger, check for water ingress at cable entry points
- Record: log in electrical maintenance record and Oil Record Book Part I if applicable
- Escalation: notify cargo control station, class surveyor if below statutory threshold, DGMA if persistent