MEO Class I · Oral · asked at MMD Kochi

What is the latest amendment to the inert gas system requirement, and what does the revised FSS Code chapter 15 require?

Short answer

Item Requirement
Threshold for new oil and chemical tankers built on or after 1 January 2016 8,000 DWT and above (was 20,000 DWT)
Oxygen in the gas delivered to the tanks not exceeding 5% by volume
Capacity at least 125% of the maximum discharge rate
Source boiler flue gas, inert gas generator or nitrogen
Safeguards deck water seal, non-return devices, pressure/vacuum breaker, oxygen and pressure alarms and shutdowns
  • Headline: SOLAS II-2/4.5.5 (MSC.365(93), in force 1 January 2016) lowered the fixed IG threshold for new oil and chemical tankers from 20,000 DWT to 8,000 DWT.
  • Before: mandatory only at 20,000 DWT and above, for tankers built on or after 1 July 2002 and before 1 January 2016.
  • Revised FSS Code chapter 15: source (flue gas, inert gas generator or nitrogen), oxygen not exceeding 5% by volume, capacity at least 125% of the maximum discharge rate.
  • Safeguards: deck water seal and non-return devices, pressure/vacuum breaker, oxygen and pressure monitoring with alarms and shutdowns, tanks at positive pressure.
  • Purpose: keep the tank atmosphere below the flammable range during discharge, ballasting, tank cleaning and gas-freeing; more tankers protected against tank explosions.
  • As Chief Engineer: SOLAS II-2 and the FSS Code apply through MS Act 2025 s.147; DGMA or its RO surveys the plant I run and maintain on a tanker.