How is propane carried and used as fuel, and which code governs it?
Short answer
| Feature | IGF Code chapter | What it does |
|---|---|---|
| Arrangement | 5 | tank, fuel-preparation room and piping segregated from accommodation and ignition sources |
| Type C pressure tank | 6 | pressurised liquid, relief valves, secondary containment |
| Double-walled or ducted piping, master gas valve, double-block-and-bleed | 9 | an inner-pipe leak is contained and detected |
| Gas detection sited low, alarms, ESD | 15 | shuts the master gas valve and trips the consumers |
- Framework: the IGF Code (MSC.391(95)), mandatory under SOLAS II-1 part G from 1 January 2017: goal-based, double-barrier, no single failure releases gas to ignition.
- Propane hazard: LPG vapour is heavier than air (relative density about 1.5) and pools low; stored as a pressurised liquid, not cryogenic.
- Arrangement and containment (chapters 5 and 6): tank, fuel room and piping segregated from ignition sources; a type C pressure tank with relief valves and secondary containment.
- Fuel supply (chapter 9): double-walled or ducted piping through gas-safe spaces, ventilated and gas-detected, master gas valve and double-block-and-bleed.
- Control (chapter 15): gas detection sited for low-lying LPG, alarms and emergency shutdown (ESD); Ex-certified equipment, purging before maintenance, IGF-trained engineers.
- Caveat: written around LNG; LPG as fuel uses the alternative-design route and the IMO interim guidelines; an LPG carrier burning its cargo also meets the IGC Code.
- As Chief Engineer: right hardware; the missing anchor is the IGF Code and the heavier-than-air point.